Air flow test in capillary tubes
rootboy
Jan 2004
Tennessee
1,375
Hi guys,
We want to be able to test air flow in capillary tubes, roughly .1" in diameter, and 3' long for the tube. Air will be the medium for the test.
Anyone know of a flowmeter that will detect obstructions (due to the brazing process when we assemble them)?
Thanks!
Differential pressure is not a bad idea.
A 'standard' tube should drop some pressure due to the small tube size. Any increase in DP would indicate an obstruction. Any decrease and you probably have a leak.
The challenge will be to have a constant upstream pressure. At a minimum a pressure regulator at an output pressure that the supply can maintain during a test. Regulators initially 'adjust' during no flow-to-flow conditions, so you need to let a regulator stabilize. If the upstream pressure varies, the DP will vary.
And there's a bunch of thermal dispersion mass flow meters the size of a pack of cigarettes, Brook, Aalborg, Omega, Sierra, Alicat, in no particlar order, usually with tube fittings for small diameter tubing.
Thanks guys!,
@Gas: I've used many a Magnehelic. I prefer to use them for dirty filter detection. And I've spent many a cold morning on the roof of the paint shop at Spring Hill trying to get that D$&! Dwyer to work. Not a fan. :)
@danw: We use Sierras here at work, the ones we use are for very low flow rates (for our leak detectors), and they do well enough for that purpose.
We tried making a obstruction tester in house (on the cheap, with no purchased parts). Using a pressure sensor on the 5mm coils I was only seeing a .2 PSI drop with one circuit blocked (50% blockage). Not too much there to work with...
For these assemblies we will have a higher pressure drop, and the flow will be lower, maybe our Sierras can work with that.
What I will probably do is to fixture the thing up, and invite flowmeter sales people in to show me how good their kit is.
Thanks again!
What's the pressure drop for a good tube?
20% of 1 PSI is 5.5" water column, which is what industrial DP's measure all the time.
Can you increase the flow rate which will increase both the 'normal' DP and the blockage DP? Do you need to limit yourself to the 'normal' flow rate when testing for blockage?
But a Brooks style thermal dispersion is probably 1/4 the cost of an industrial DP transmitter.
Root boy,
We have used those sensors to test for leaks on automatic glass making machines and they have always been very reliable.
BUT...they were inside and everything was relatively clean.
Root boy,
This one was outside on a Thermal Oxidizer, and it would always fail during the dead of winter. So it would either be freezing, or just a gentle winter rain when we had to fix the thing. :)
The unit had been swapped out several times for new ones, but it would always shut down in winter.
I don't know as of yet. This was a project that belonged to one of our guys who moved on to greener pastures. He's now living in the UK. :)
We like to do a leak test at 60PSI first. And I see no reason to use less pressure for the flow test. But if I'm stuck using the small Sierras, then it will probably have to be lowered. Or add a second flow meter for the obstruction test.
Thanks! I'll have to check them out.
Hello ! I need help to understand these arrows on this solenoid this solenoid is activated electrically by 110 VAC and it is being used to...
1,916
On site we have Yokogawa EJA110E differential pressure transmitter connected to process air line. I'm not sure if this can be used to measure air...
4,421
Hello, I'm building a system for my professor and for controls I will be using a PLC from automationdirect as a way of getting into the field and...
1,746
Hi all, I have an application where I have to measure air flow through a HVAC duct, as we have to ultimately maintain a certain rate of air...
3,237
Dear all, I have air compressor having flow rate 3 cubic meter per minute as mentioned in the name plate. I have started this compressor at 9:00AM...
2,653