AL1920 losing IP address
stretch_af
Mar 2011
Drinking in Wisconsin
69
5069-310ERM controller Ver31
This new machine we have has 3 IFM AL1920 IO-Link masters in it, all in the project tree in the processor. For reasons unknown, 2 of them like to randomly change their IP addresses.
One went from: 192.168.1.20 to 192.168.1.250.
The other went from: 192.168.1.21 to 0.0.0.0.
This has happened twice now. Set the IP address to what it should be and all is good.
Has anyone seen this with IFM IO-Link master devices?
Can other things in the panel change an IP address?
The panel is connected to a larger plantwide network, but that goes through a 1783-NATR first, and only the PLC is setup in that.
Justin
What switch are you using? Some switches have DHCP persistence. Meaning that you can assign an ip address to a port, devices plugged into the port will be assigned the port IP address. It’s a little more in depth than that buts the high level “this could be possible”?
The switch is an N-Tron 716TX. I am not familiar with the N view software for them, working on that. But they don't seem to be set up to push IP addresses.
The problem devices are set for static addresses also.
Generally.. unless there is some curious setting for Static Unless Collision (which i've never seen) a Static configured device will never change its own address. Consider setting it to dynamic, having it acquire and IP or fail and gain a 169. series address, then switch it back to static and give it the proper address. I have on rare occasion seen devices be set to static, and not be set there internally, as if some leftover bit in the user interface side is effectively lying to the operator.
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
192
Hello all, I have a question in regards to RSlogix 5000. I am having issues with the program force closing when I try to make online edits. We...
132
I am working with beckhoff plc in twincat 3 environment. I have a array of struct which I want to make persistent. I declared it with...
116
We have a quad monitor setup with FT SE and we are utilizing a header screen at the top of every display. when we open a new page we abort the...
103
I have a Siemens 1515 controller with the configuration of cards (input, output, safety input, safety input, safety output). I am having an issue...
188