Alalog Output Scaling, Please help !
richleva
Sep 2012
ontario
79
Hello,
I need to control an Acid pump at a water treatment plant, Using an analogue output of a micrologix 1400. This PLC only has 0-10V analogue output card. So I installed a 500Ohm resister across the pair of my instrument cables, to get my 4-20Ma. So at 2Votls will be my 4mA and 10 Volts will be 20mA.
PLC Resolution (0-4095)
Acid pump 1
0-60 L/H
Acid pump 2
0-12000 strokes per hour
In The PLC. I'm using RXLogix micro developer, and I'm using the SCP instruction to scale
I tried using one SCP block, but the input number that is entered is much lower than what is display in the pump
Example:
F8:1
input: F8:1 --->> entered 7 l/h in the HMI
input min: 0
input MAX: 60
scale min: 819
Scale max: 4095
Output O:0/0 --->> Pump said about 12 l/h
I tried using two SCP block per pump, to scale input number from the HMI to 4-20 and the second would scale the 4-20 to the PLC 12 bit analog card (4095)
but I got similar results...
SCP 1
Input: F8:1 ---->> entered 15l/h in the HMI
input min: 0
input MAX: 60
scale min: 4
scale max 20
Output F8:2 ---->> 8 mA
SCP2
Input: F8:2 ---->> 8 mA
Input min: 4
input max: 20
scale min: 819
scale max: 4095
Output: O:0/0 ----->> 1638
The results for example
today I entered 30 L/H in the HMI the pump said 41.8
for the other pump I entered 6000 strokes per hour, pump would say 12000 strokes per hour.
PLEASE HELP, if anyone has ideas....
Thanks everyone
The 1400 analog output can only source into 1000 ohms or greater. The 500 ohm resistor is loading down the output so you will never reach full scale.
Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
70
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
144
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
110
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
319
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
86