Have some equipment that have the micrologix 1400
1766-L32BWA. all of our equipment in the locations have 208-220vac 60 hz power.
Was just told we need to relocate some of the machines to a location in Vietnam. We was told the availiable power in the Vietnam plant is 180-200VAC 50HZ.
Will these PLC's run off of this power? We relocating about 9 machines that are used in production.
Thanks