Allen-Bradley 1783-natr problem with public network

TIA5000

Member
Join Date
Aug 2020
Location
inside PLC
Posts
5
Hello everyone,

I face a problem with setting connection between my computer and PLC using NAT addressing.

I configured NAT. In private network it's everything fine.

When I am connected to public side of my network I can:
* use VNC viewer to control my PVP HMI
* open NAT configuration webserver
* ping NAT, HMI and PLC (devices with assigned mapping) using cmd.

What I cannot do in a public network:
* find this devices in RSLinx
* connect to the PLC using Studio5000

Do you know where the problem is?
I assume either in NAT config or in RSLinx adapter settings.
 
You are probably using the Ethernet/IP driver in RSLinx. YOu need to use the Ethernet Device driver.

this has to do with how Ethernet/IP auto-discovery broadcast. It doesn't survive the local subnet.
 

Similar Topics

Good Morning everyone. Trying to install a 1783-NATR comms module on a system with a CompactLogix L32E processor, An unmanaged switch with a 3rd...
Replies
4
Views
3,145
Hi friends, I need to check a process, so, I need to connect with some instruments through the switch stratix 1783 Allen Bradley. The instruments...
Replies
0
Views
2,612
Any one give solution for this fault. We are using AB Gaurd logix controller(5573s), resent days we are facing major fault in controller...
Replies
1
Views
52
Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
Replies
15
Views
333
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
Replies
3
Views
98
Back
Top Bottom