Allen Bradley 1784-NATR

Azard

Member
Join Date
Jun 2020
Location
Minto
Posts
3
Hi,
We have six 1783-NATR. Two of them can be accessed by the vendor is outside of out plant network via vpn. The other four cannot be accesed. All of them can be accessed by the plant network. Thank you
 
I have gone through many times but I cannot find any significant difference between them. The only difference is for the working two, the private network is plugged on the front interface and the other four is plugged on the rear interface. But those should only affect the device in the private network right? Unless the reply is from the private interface.
 
The two ports on the bottom of the 1784-NATR are part of an embedded switch that supports Device-Level Ring (DLR) fast fault tolerant ring architecture. It sounds like you are not using the DLR feature.

The device's "Private" LAN interface has only one IP address, even though there are two physical ports and two MAC IDs.

Generally when any TCP/IP device can't be accessed via a VPN or network bridge, but can be accessed from an address on the enterprise network (often in the building) it is because the Default Gateway address configured for the device does not specify the gateway correctly.

But your devices that you posted screenshots of (thank you !) have the same Default Gateway configured for the enterprise network side: 192.168.140.254.

I presume you've checked the devices and are sure the OK LED isn't flashing red, indicating a duplicate IP address. Such conflicts will also show on the Address Conflict Detection tab.

How many 1:1 NAT address "rules" do you configure each device for ? I noticed that the devices are only two host numbers apart (192.168.140.65 and 192.168.140.67).

Have you been able to try changing the Private physical connection for the 1784-NATRs that can't be accessed via VPN to the bottom-forward interface ?
 

Similar Topics

I have PanelView Plus 600 with the card slot that supports 1784-SDx and 1784-SDHCx SD cards. What're any compatible analogs?
Replies
3
Views
2,283
hey guys. having some problems with my driver to connect to the SLC 5/04. I can configure it in rs linx, but when I go into rs500 to download the...
Replies
1
Views
1,408
HELP!!! I have an Allen Bradley 1784-T30G terminal. The program got dropped. I have the binary program but don't have a user manual to figure out...
Replies
0
Views
1,303
Does anyone know of a Generic brand that works as well,the price on these are out of my price range thanks in advance for any info ..Mer
Replies
2
Views
3,896
Hello! We use a lot of different PLC brands (e.g. Allen Bradley, Siemens, Mitsubishi, Keyence) in our products. For that reason, we decided to...
Replies
2
Views
7,579
Back
Top Bottom