Allen Bradley CPT Instruction
Ones_Zeros
Feb 2014
at work
367
Hey Everyone
I was wanting to get some advise on the math below on this expression
for a SCP instruction
(75.0-10.0)*(Suction_Pressure-4000)/16000+0.0 = 10.37
My transmitter is scaled +75 to -10
how would i change the above expression to include the -10?
the result should come out to around 0.2
thanks
I'm sorry i meant to say CPT instruction
been long day
I have the SCP add on instruction downloaded but I would have to take the process down to download it into the controller
i apologize
Well, I solved for Suction_Pressure and got 4255.26 - is this correct for your system?
Math-wise, I saw two options:
1. Change (75.0-10.0) to (75.0+10.0). This gave a result (with the above Suction_Pressure) of about 1.35.
2. Change the 0.0 at the end to 10.0. This assumes that the original expression can be written ((75.0-10.0)*(Suction_Pressure-4000)/16000)+0.0. This, of course, would give a result of 0.37.
Do either of these look like they would work for you?
Yeah,
the end result I was looking for was around 0.2
raw suction_pressure value = 6553
(75.0-10.0)*(6553-4000)/16000+0.0
so would i change the +0.0 at the end of the equation to -10?
thanks
Yep, I went back and did it over again. If I read your original formula correctly (that is, it can be written with the extra parenthesis as I did), the +0.0 at the end of the formula can be changed to -10 to provide an answer of 0.37.
Again, this is just me looking at math. I may not be looking at your process correctly.
Hello Mickey,
(((Scaled Max-Scaled Min)/(Max Raw Input-Min Raw Input))*(Raw Input-Min Raw Input))+Scaled Min = Scaled Value
Since my scaled Min is -10 & scaled Max is 75
Would I still enter this in the expression as 75-10 or 75 - (-10) ?
(75-10)*(6553-4000)/16000-10 = value
1: You can import AOI's online, unless there are versioning differences. If there are, open the AOI in a demo program offline, create a new one in the online program, and copy every thing over, manually if necessary.
2: This is simple math. If you want to see how it works, plug it into Excel or something similar, and play with the numbers.
Seems I'm have issues inputing my data into the formula to get the correct value.
The final value should be around 0.2 to 0.3
the data is
scaled Max = +75
scaled min = -10
Raw In = 6546
Max raw input = 16000
Min Raw input = 4000
the final value should be around 0.2 to 0.3
i just want to make sure i plug my values into this expression correctly
Thanks for the help
where did you get those numbers? ...
the scaled value that I get for an input of 6546 comes out to 8.034 and change ...
but then again - maybe the formula that you're giving here is not a "standard" y=mx+b ... I'll take a look at it when I get some spare time ...
The math doesn't lie...
You have provided incorrect scaling data to achieve what you are looking for
the data is
scaled Max = +75
scaled min = -10
Raw In = 6546
here is what i know & what normally we have scaled the setting on the
1769-IF8 analog card
the transmitter is scaled +75 to -10
so this should be my scaled max = +75 and min = -10
the input Max = 16000 & Min = 4000 (based on the scaling setting on the 1769-IF8 analog input card) I might have these wrong
the Raw input 6546 is the actual 4-20ma raw value coming into the card from the transmitter
the actual read out on the transmitter is somewhere around 0.2 to 0.3
so based on the scaling on the transmitter i know this is what my final value needs to be after working out the expression
I may not have these values correct since the expression is not working out correctly
what ever i need to change on the expression, please let me know
thanks alot i appreciate you guys looking over this
Are you sure the transmitter is actually displaying a true value?
You can't quite presume the transmitter is "good" by default; instrumentation needs to be 'digitally" calibrated but not before empirically proven to be true.
Measure (using dedicated means) the respective physical variable: Pressure -> Manometer; Temperature -> Thermometer; Distance -> Micrometer/Caliper, etc.
After empirically establishing the present process variable value, measure the sensor's electrical output signal value corresponding to the present physical value (mA meter for current devices or V meter for voltage devices).
Only after the two steps had been completed and proven to be accurate one should go to the next step and acquire the true digital value within the controller application.
367
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
93
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
623
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
441
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
145