Allen Bradley CPT Instruction
there are several ways to set up the scaling for your input module ... we're not sure which of these setups you're using ... and (no offense) you're not really sure of what values are being used ...
now for the classic question:
are you allowed to post the ENTIRE project file (ACD extension) ... we can move along a LOT faster once we see what's behind the curtain ...
you might also put a milliamp meter in the circuit - and tell us how many mA are actually flowing through your module's input ... (that would probably be easier than working with the transmitter - at least at this point of the game) ...
and by all means - confirm that the transmitter is putting out the correct value ... (maybe it has various settings and adjustments that aren't quite right ...
here is what i know & what normally we have scaled the setting on the
1769-IF8 analog card
the transmitter is scaled +75 to -10
so this should be my scaled max = +75 and min = -10
the input Max = 16000 & Min = 4000 (based on the scaling setting on the 1769-IF8 analog input card) I might have these wrong
the Raw input 6546 is the actual 4-20ma raw value coming into the card from the transmitter
the actual read out on the transmitter is somewhere around 0.2 to 0.3
so based on the scaling on the transmitter i know this is what my final value needs to be after working out the expression
I may not have these values correct since the expression is not working out correctly
what ever i need to change on the expression, please let me know
thanks alot i appreciate you guys looking over this
This may help you....
Split up your equations for sanity sake.
y=mx+b
Solve for X otherwise known as RATE:
X:=(rScaled_Max - rScaled_Min) / (rInput_Max - rInput_Min)
Solve for B otherwise known as OFFSET:
B:= rScaled_Min - (rInput_Min * rRate)
Solve y=mx+b using previously calculated X and B values:
Scaled_Output:=(iRaw * rRate) + rOffset
So you are using Engineering Units, respanning 4-20mA to 4000 to 16000? Why is this? I would do this with 4000 to 20000 for 4-20mA signals.
here are some of the ranges available for your 1769-IF8 module ...
we can't do much more than guess until we know which of these setups you're using - and how much current (mA) is flowing through the input channel ...
good luck - I've got to go cut the grass now ... (spring has sprung) ...
361
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
92
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
612
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
431
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
145