Allen Bradley DH485 Network

rohit_plc

Member
Join Date
Jun 2013
Location
delhi
Posts
81
I have an allen Bradley system in which there is two micrologix 1200 and two panel view 300 and a Rsview 32 connected on DH485 network with the help of 3 no.'s of AIC+. both panel view 300 now dead. we have 2711R-t4t. can we replace this with panel view 300 ? will it work in this network configuration ?
 
Yes, the Panelview800 supports DH485. There is no direct migration path for a Panelview to a Panelview800. You will need to create the program for the Panelview800 from scratch.
 