I have a ML AB 1400 which i am currently utilizing the ethernet port to communicate with. (HMI,PC,Etc.) My question is can i bring in device information from a third party device via modbus on the controller and still utilize the ethernet port as well? And if so can I incorporate that data directly to my program?
Do you want to use the Ethernet port configured for Modbus TCP? How is it configured now?
Channel 0 and channel 2 can be configured for Modbus RTU slave or master if you want, in addition to using the Ethernet port. All ports are independent of each other.
The data received can be used in your program.
I currently use the ethernet port as ip only for the HMI as well as prgramming. The device I would like to bring in is a generator which only has a modbus RTU port. So I would like to bring in that data and incorporate it to my programing and still be able to communicate with the plc through the HMI via IP.
That should work for you. As Mickey said, all the Ports are independent of each other. Any Data you bring in from the Generator will also be available to the HMI with proper Data Formatting.
Stu....
Definitely. You can configure either Channel 0 or Channel 2 for Modbus RTU Master, and use MSG instructions to read data from the generator.
Channel 0 has both RS-232 and '2-wire' RS-485 signal pins, and Channel 2 has only RS-232.
Hi, Iam Working in a project where Micro850 and Epson ROBOT is there, I need to read and write bits to and from ROBOT. Iam Using TCP/IP and...
1,278
Hey guys, I'm working on a proposal for a client, and long story short I need to suggest a new master PLC for polling existing RTU sites that are...
23
9,856
I have the Allen Bradley ControlLogix PLC on a working installation. I want to exchange data to DCS (master system) via Modbus TCP protocol, but...
17
8,564
An ex-colleague dropped this on me and threw me for a loop. Am I wrong in asserting that no PanelView terminal including the 800 is Modbus...
4,796
Hi guys. I have a some-what noobish question. I have been doing light plc programing for the last year or so, mostly with descreate I/O's, simple...
3,853