Hi,

We use 1771-OBN/B output cards.

On one rack, HALF of all the output cards have gone off.
(LHS active but RHS gone off)

Please help !

Thanks.
 
Last edited:
Hi,

Thanks for replying !

The program shows outputs as active but the RHS of each output card is completely off.

There has been power problems onsite, but all PSU's are now OK.

It seems to be an addressing or software issue.

The 4 output cards each have 2 banks of 18 outputs and are located in slots 9/10/11/12.
 
Can you zip and attach a copy of the program to a reply? (The forum only allows certain file types, and .zip is one of them.)

You say you had a power problem, it's possible that the backplane comms chip was damaged. Now your power supply is okay...rack power supply or external for I/O?

Have you verified that your new power supply is performing correctly?
 
We cannot attach the program.

PSU is a 1771-P7 and is OK.

Slot addressing is 1/2.

Analogues are OK, but Dig OP's still halved. (LHS on / RHS off)

All other cards OK, so assume backplane is OK.
 
The DC Output Cards (1771-OBN/B) are 36 way.

00>17 and 00>17 again. (on each card)

The first 00>17 (LHS) are working and the second 00>17 (RHS) are off.

LHS - Left Hand Side
RHS - Right Hand Side

Thanks again for trying to help us. Having a nightmare.
 
FYI
Your card is a 32 point card. Note outputs 8 & 9 are not there.
PLC5s use an octal numbering system for it's input and output cards.

What do the status indicators on the card tell you? Also the fuse indicator on the card.
 
Last edited:
Well, the only thing I have noticed after reading through some literature is that they are not compatible with series A chassis.

Is the I/O in RLSogix5 showing to be okay (not faulted)?

Do you have a spare chassis you can try?

So, with 1/2 slot addressing, this is outputs O:22/0 through O:31/17, correct?

When you monitor the output image in RSLogix5, are you seeing values appear in each cards' 2nd group?
 
Last edited:
Thanks.

Fuse Indicators not lit. Same on other PLC's that are OK.

On all output cards first 00>17 are working, but second 00>17 off.

??????????????
 
Okie..

We have no spare chassis.

You are correct in the addressing. It seems to be that the software is only aware of half of the outputs ???!!
 
Thanks.

Fuse Indicators not lit. Same on other PLC's that are OK.

On all output cards first 00>17 are working, but second 00>17 off.
s
??????????????


Have they ever worked? Or did this just happen after the power problems?

Can you unseat and reseat the modules?
 
Last edited:
Are you certain you are addressing the outputs correctly.

You said that the output cards are in slots 9, 10, 11, and 12.
How have you determined the numbers of these slots, by counting from the first I/O slot as 0 or 1 ?

Here is a map of the rack showing the slot numbers...

2011-08-14_164052.jpg
 
Last edited:

Similar Topics

Does anyone have the installation files only (not the license) for the Allen-Bradley 6200 software for the PLC 5/250 (also known as Pyramid...
Replies
3
Views
1,216
Today I was making an online edit to a 5/40 Series E Rev K.2 with about 14% free memory. I was removing one branch in a large rung. Accept...
Replies
4
Views
3,171
I am using a legacy Allen Bradley PLC5/40E Series F CPU Having issue with compute instruction syntax with the expression Doing a divide by...
Replies
7
Views
1,771
I have been working within a file for several days and this morning I am getting a "Access Violation to Current Processor" error? I was just in...
Replies
1
Views
1,916
Hello, We use 4 racks with 1785-L80B, 1785-BCM and 1785-BEM in them. I am looking to purchase secondhand a few spares as we have had some...
Replies
4
Views
2,210
Back
Top Bottom