Allen Bradley Ultra3000 E11 error
jcsbnsx
Aug 2015
Texas
Ok so first allow me to bow my head and say I'm a retired mechanical engineer and while I still have a few brain cells left there is something I think I'm missing in the setup.
I have 2 Ultra3000 servo drives and 2 Mpl servo's. Regardless of the combination I'm getting the E11 error which has to do with the phasing not being correct. I've double checked the wiring harnesses and changed the orientation of UVW. Nope, nothing helps. Both of the drives are used but appear to be in operational condition (I have no direct history on them).
I have not tried to communicate with the drives through any program. This is where I'm falling short. Could the drives been programmed previously so that they don't recognize the servo's? Any suggestions would be greatly appreciated.
John
I’m with Geoff on this one. Most drives have an encoder feedback “invert” bit that needs to be set to match the direction of the encoder, to what the drive expects to see.
You would have 4 possible scenarios.
Motor wired, invert = 1, drive faults.
Motor wired, invert = 0, drive does not fault but travels in the wrong direction
Motor rephrased, invert = 1, motor runs intended direction and does not fault.
Motor rephrased, invert = 0, drive faults.
Thinking about it again if you rephrased is still got the alarm I bet you have no feedback at all. Check your feedback, hall/encoder connections.
E11 is an error for Hall phasing, not power phasing (although if _Dock_ is right and it's checking encoder phase against actual motor connections, then incorrect motor phasing could cause the issue to show up).
It's almost certainly an issue with your feedback device, wiring, or settings.
First post here I have an ultra 3000 010 servo drive ,I'm using an AB mpl a420p-h servo, when I am configuring in ultraware, I select the motor...
1,489
Morning... Need your help... I have one unit allen bradley ultra3000 which is fault/error. The error is when power ON, the Green & Red led were...
2,401
363
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
92
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...