Hi everyone,
I have a new (for me) situation with a new job I am working on.
I am using the output channel of a 1769-IF4FXOF2F card to send a 4-20mA speed signal to a VFD. The manual for the drive says that the analog input channel is sending the loop power out and should not be connected to an external supply. So in the Analog Input is a Active Input. The IF4FXOF2F is also a Active output. Neither of the 2 seem to have a jumper or switch that will change it from Active to Passive. So how do I interface these 2 together without frying something?
Is there anything on the market that will take a Active input and make it passive on the other side?
I would appreciate any help you can offer.
Thanks,
As per mickey's post, what you want is called a loop isolator.
What model of drive, that's quite an unusual feature? For it to be an active input with loop power supplied by the drive, the "negative" end of the input would be internally tied to the drive 24VDC power supply zero volt rail.
You may be able to make this work by wiring the analog output negative to this zero volt / common terminal. But I'd want to see the drive manual before recommending that.
Thanks Mickey and Saffa,
Loop Isolator, that is what I needed to know. The drive is a Phase Technologies APG series. It is a older drive that is no longer in production.
Looks like AutomationDirect.com has a Isolator (FC-11) that should do the job.
Thanks again!!
I am currently working on a job where i am recieving a 4-20ma signal from a tempreature controller. the signal is steady but the value in the plc...
4,511
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
116
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
129
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,145
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259