Analog from SLC-500 remote rack to PLC5 main rack

matt.norsask

Member
Join Date
Mar 2016
Location
Saskatchewan
Posts
16
My goal is to get an analog signal from a SLC-500 remote rack back to a PLC-5 main rack. Is this possible? If so, I may need some help. I've set up a BTW and BTR, but I can't seem to get any readings from the NI4 analog input card. Any ideas?
 
Thanks for the help, Jesper! The manual pointed me in the right direction. My issue ended up being in the dip switches on the 1746-ASB module. The image size was set to 4, and since the NI4 card was the 5th, the adapter didn't realize it was there. Simple fix for someone experienced, I'm sure. The rack was already in 1 slot addressing, so I used a BTW and BTR pair to make the card communicate. Thanks again!
 