Analog input 1746-ni16i status light
Buzzen
Apr 2010
stockton, ca
132
:skuller:HELLLLO TO ALL,
HERE IS THE PROBLEM I HAVE ENCLOSED A ZIPPED FILE FROM THIS APPLICATION. THE PROBLEM I AM HAVING IS THAT THE STATUS LIGHT FOR MY INPUT SLOT 11 IS BLINKING. CHECKING STATUS BIT FILE 14-15 I NOTICE THAT 14 IS 1. WHICH ACCORDING TO THE MANUAL IS AN ERROR. I CAN'T FOR THE LIFE OF ME FIGURE OUT THE PROBLEM. IT IS INPUT 11.1. PLEASE HELP.:eek:
Is it just the Module Status LED that is flashing ?
What is the state off the four Channel group Status LEDs ?
Has this module been running for a while and stopped working correctly, or is this a new startup of this module, or were you doing any other process (calibrating, maybe?) when the error started ?
Module status light is solid green okay there. The channel 0-3 light is blinking. In the book is says that the scaling could be wrong and that would cause the error light to flash.
This is a new startup. My first actually. I did an read I/O configue on initial startup and initialized the input and output cards. Is there an additional step that I am missing?
Going from poor memory here but is there a signal on those points? If not, try to put a signal on a point and see if it stops blinking.
[QUOTE][/QUOTE]Well first of all in the file you posted channel 14 is not enabled. Only 1 thru 4 are.
Sorry for the misunderstanding I was referring to the data file for that card. Not the channels. In the SLC 500 Analog input card users manual I am looking at page 5-4 and it says that you need to set bit 15 to a 1 to enable that channel. Am I reading that right?
Yes I put a meter on the channel and forced a 4-20ma signal and still that little light keeps blinking.
Hi everybody Does anybody have experience with the Analog input card 1746-N18? Cannot get the last 4 inputs (4-7) to work like the first 4 (0-3)...
2,970
Hi everyone, I have a SLC 500 (5/04) with a 1746-NI8 Analog module input. I have two questions: 1. I have noticed there is a IN0-, IN0+ and...
3,504
I am adding scale weight inputs (4-20MA) to a existing program, using analog input card (1746-NI16I- Class 3). Processor is 1747-L542C 5/04 CPU. I...
8,573
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,141
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259