analog Input 1769-IF4
faiek
Nov 2009
Ontario
Hi All,
Would you please assist me to use GSV instruction to obtain the value of analog Input from Ch#1 of 1769-IF4?
That's not what the "GSV" instruction is for. Its to monitor controller status. See PDF below for more info.
Depending on what processor you have see link below appendix "B" and "C" for how to access the data from the module.
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1769-um002_-en-p.pdf
Thank you so much, Please note that I'm using processor 1769-L32E, would you please provide me with a simple example of how to retrieve the input value of the analog module and compare it with the set value.
Regards,
You would read the tag corresponding to the slot and channel for your I/O card. The analog input value for an analog input module in slot 4 of the local rack would be in the tag:
Local:4:I.Ch1Data
Depending on how you have your card configured, you will have to apply some scaling factors to get that value into real world units. For example, I have my analog card set up as 4-20mA, engineering units. At 4 mA, it will read 4000 and at 20 mA, it will read 20000.
Local:4:I.Ch1Data
Thanks, I know how to monitor the Tag and how to configure the Input.
In my example I set the Input Ch#1 to 0-5V which represent the motor speed feed back I would like to set Alarm Lamp when the Speed reaches 4.5 out of 5.
Your response much appreciated.
Hi, I'm using an Allen Bradley 1769-IF4 Analog input crd with a Compact Logix L33ER. Its 14 bit (0-16384), and I'm taking raw readings. I am...
4,596
Hi, I need some help reading the value of Channel 0 of a 1769-IF4 card. The analog card is in slot 1. So the Input value should be...
3,951
dear All. I have one module analog 1769-IF4. I read manual, I saw every chanel ( CH0-->CH3) it have 1 word for configuration operation. such as...
5,252
After reading the 1769-IF16C compact Logix analog input current module field wiring connection we noticed that it be used only with 2 wires and 3...
7,946
Hi all, I have a 1769-IF8 Analog Input Card in a Micrologix 1500 system. The card does not read any inputs. I already checked the wiring and it...
6,001