I am using a 1769-IF8 analog input with a 0-10volt load cell input. When I configure the input to 0-10v, it always reads as 0. When I configure the input to -10v to +10v, it reads negative numbers. Even when the input is 0 volts, it still reads a negative number. I checked the input with a meter and it is reading and positive voltage.
You are reading noise on the line. The signal to noise ratio at 0 volts is infinite.
When the setting is at 0 to 10 volts the PLC will clip the noise in half because it cannot go below 0.
Regards,
I would have thought that the numbers would jump if there was noise. They are pretty steady.
They will be jumping around if you are viewing on a oscilloscope or similar device. You could minimize the amount of noise on the analog line by installing a capacitor from the analog to ground.
gclshortt,
Wouldn't installing a capacitor from the line to ground defeat the purpose of an analog input?
when the capacitor charges to 5 volts lets say, it stays at 5 volts until it discharges?
regards,
james
Whats the reason for configuring -10 to +10 if the load cell is 0-10 then you should only use 0-10 and not -10/+10?
Let's look at simpler reasons ...
If a greater weight causes the signal to move in the negative direction then either the excitation or signal leads to the load cell are backwards.
If the signal is negative but moves in a positive direction (less negative) with more weight then the offset is incorrect.
I put it at -10 to +10 just to see what the values were.
If you dont use what the manufacture set it up for then you will get funky values... Just like if you used 0-5 you would think it would just go to 5v and stop but it wont most of the time... if you dont want it to go below 0 then put a MOV in your logic and write a =/< (equal to or less than) MOV 0 to the register and it will never go negative
I find 0..10V quite high for load cells. The typical load cells that I come across get a 5V or 10V excitation voltage. The signal voltage that comes back on inputs is typically between 5mV and 30mV for max load on the load cells.
I missed that the OP didn't mention a load cell conditioner. Yes, attaching the output leads of a loadcell to an ordinary analog input card probably won't work very well.
Could you perhaps provide a model number for the load cell and a diagram showing how you have it wired to the card?
Hello, I have a Micrologix 1400 PLC and using RSLogix 500. Using a Multi Ranger Ultra Sonic Level Sensor and the input is moved to N7:11, then...
3,897
Please can anybody recommend a way of measuring a negative voltage (-40 to -60V dc) on the analogue input of an Allen Bradley Micrologix 1100 PLC...
2,850
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,143
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?