Im a little rusty regarding S7 and analog value processing atm so I hope I could get some answers.
What is normally the fault when getting overflow on analog value from a sensor ?
On underrange/underflow its broken wire etc. but on overflow what will the cause most likely be?
If you are talking mA loop then an overflow is too much current. Current depends on Voltage and Resistance, so if the voltage driving the loop is too high for the sensor to control, or if the resistance of the loop falls too low, maybe because of a short circuit. Also for mA systems ground loops can cause both failures, it is where the 0V on the sensor and PLC aren't at the same potential.
But ground loops is only relevant if the instruments are powered by the 4-20 mA ? And not by external power supply?
Either one can get ground loops. The instruments with an external power supply by their design have a separate 0V, and unless the 4-20ma output is isolated from that 0V, or the PLC input is isolated from the PLC 0V, you will likely have problems unless the 0V can be tied together.
You can also get ground loops in a 4-20mA loop when a loop powered sensor isn't isolated. Fast sensing thermocouple sensors are often electrically bonded to the case and so need isolated converters to avoid issues. I had problems with a guided radar level sensors, it was fine when one was powered up, but if a second was used on a tank that had the same earth as the first they both gave the reading of the fullest tank.
There is an argument that you can avoid ground loops by not grounding anything, for me it is like saying you shouldn't earth any metalwork on a machine to avoid electric shocks.
Hi everybody, I inherited a redundant 1756-L71 ControlLogix system with 2 racks with some DI, DO, and AI redundant modules (1715 series). The...
2,423
hi I have to take average of my analog input data from analog input module FX 2N-2AD using with FX1N plc. As I cant treat REAL NUMBERS in FX1N...
2,035
I am new to this analog stuff and am having problems understanding the value or scaling or ?? when passing data between an analog input card and...
11,344
Hi everybody. I have a CompactLogix system with some 1769-IF4XOF2 analog input modules that has an strange behavior. Its analog values changes...
3,138
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,143