Analog Input Wiring
coopdegrace
Mar 2009
perth
34
Hi All,
Probably and easy question for some but I am struggling, so any help appreciated.
I have an AB analog input module number is 1794-IF8IH.
We have a couple of flow meters with 4-20mA HART outputs that we want to read.
Does the analog loop require an external power supply or will it get this from the module? i.e. can I simply connect the +ve and –ve terminal of the flow meter analog out to the analog input channel?
I appreciate any help
Cheers
If your flowmeter is a four-wire current transmitter, you don´t need an external PS.
If your flowmeter is a two-wire current transmitter, you need an external PS.
nonuke maybe slightly nuked, as the answer is the opposite of the above.
2 wire the unit will be supplied via the PLC, using just the 2 wires supplying the 24 volt (normally) and reading the current with the same wires.
4 wire will be powered from and external PS, 2 wires for the supply, 2 wires for the current signal back to the PLC.
So you can understand the 2 wire and 4 wire system. The image is the 1794-IF8IH.
Maybe l had some radiation, happy to stand corrected on that module, l new l should have googled that module.
A Siemens Coriolis flowmeter is a 4 device requiring a separate power supply to make a meaurement.
But it's 4-20mA output can be either 'active', powered by the flowmeter's power supply (4 wire) or 'passive', powered by an external power supply (2 wire), as ordered from the factory (not field selectable).
The model number defines which (of one or more AOs) is which, passive or active.
I've seen other flowmeters that are 4 wire but the AO is passive 2 wire output.
The bottom line is you need to check the flowmeter's documentation to see whether the AO is active or passive.
+1
Endress Hauser flowmeters are the same way, can be source or sink. Need to check the manuals.
Firstly thanks all for your help, much appreciated.
From the 1794-IF8IH manual it tells me the Transmitter can be wired directly to terminals A0 and A1, and power wired to terminal 34(+) and 35(-)
So I do not need to provide power to the loop as it is supplied indirectly via terminals 34 and 35
Have I understood this correctly?
Cheers
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,205
Hey guys, I've only dealt with wiring 4-20mA analog inputs as the majority of instruments I've used are 4-20mA. I'm using a Mitsubishi VFD and...
1,161
I am trying to wire four analog signals to a analog input module AI 4xU/I 2-wire ST (6ES7134-6HD00-0BA1). When I turn on the first device...
6,682
Could someone show me an example on how to wire the analogic input for lets say channel 0 ?? Ive found this manual...
5,240
Hello, I am so confused now with the analog input module wiring. I am about to use a 9900 GF Signet transmitter for my analog input. I saw the...
5,477