Analog: Not should I, but can I?
You need to add wire resistance to internal components resistance....
I have seen that kind of unsafe use of 4-20mA loop with an extra power supply in the middle of the run to boost the voltage. as long as everything is isolated from ground or any system reference voltage it would work....
It is hard to point which one is worse but this is another option. You can even use duct tape to hold the extra power supply on one of the drive panel to make sure it looks odd.... :)
I would use signal isolators/duplicator to do a cleaner and safer install for that kind of things as suggested. This would also keep the signal to other components if you service one....
Thanks for the info. Conductor resistance was taken into account, and I consider it negligible in this circumstance, as there is less than 40 feet of conductor in the entire loop.
hello.. i wanna add the value of an analog input value to the PLC existing system in my plant, i use OMRON CS1G-CPU45 and the analog input module...
3,691
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
116
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
129
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,145
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259