Here's what I just did, and it worked for me right away.

I open Do-more Designer, Create a new Offline Project, Do-more Simulator.

Create a new Device, Modbus TCP Client, "ClickTest"

Add two MRX instructions to $Main, one reading coils, one reading holding registers.

Populate Click's IP address, coil offset and length, holding register offset and length, etc.

Write to Simulator, and put Simulator in Run mode, enable X0, and it works for me.

Click Modbus TCP Simulator.jpg
 

Attachments

  • ClickModbusTCPTest.zip
    25.9 KB · Views: 1
Thanks for your help Bolt

I ended up calling AD tech support (very nice and smart guy) we tweaked a things and it still did not work, after wasting over an hour of his time... ended up as a bad Ethernet cable, I changed it yesterday because I suspected it and can you believe I had two bad cables?, we took the one from the Click and it started working I grabbed a used one I had (known good) and they started talking to each other

Learned a lot, check the basics first :oops:
 

Similar Topics

I had a project possibility fall in my lap yesterday, and I spent some time trying to figure out the mechanics of sending a couple values between...
Replies
12
Views
4,863
I am trying to find a way to get a CSV file from the micro SD card in the BRX out to a USB device without having to have a computer attached to...
Replies
4
Views
2,349
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
Replies
1
Views
133
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
139
Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
21
Views
573
Back
Top Bottom