Averaging values with A Controllogix L61
440_Man
Jan 2016
Iowa
I have a process that is using a mV signal to control a PID loop. Currently, the mV signal is experiencing a +/- 1 mV noise. In this process, +/- 1 mV is a tangible change. I would like to take a sample of ten mV readings every second, then use the average of those ten readings to control my process. I am fairly new to ControlLogix, so detailed help with the instructions would be appreciated.
thanks,
440_Man
IF4XOF2F/A analog card
Digital filter for the mV input is set at 1000 milliseconds
RTS for IF4XOF2F/A is set at 25 ms
PID loop is in a periodic task set at 100 ms time period
Report Post
If you have access to Function Block, I have used the LDLG instruction to do filtering. You can adjust the Lag parameter to get the desired result.
That card is not made to measure mv. The resolution is probably your problem.
See PDF
Thermocouple input modules have mv ranges.
Mickey, my range is from approximately 800 mV to as high as 1.500 volts.
Is there a better card for my application?
Found the formula FV=FV+C(NV-FV) while digging through the forum. I will implement this and let the process run a few hours to see if this filter will work for me.
thanks for the help!
A mv transmitter may be a better option, that would give you an input in the 4 to 20ma range or 0 to 10 volts etc.
Hi, I have a bit of PLC experience in Siemens and have unfortunately been blessed with working on Automation Studio and B&R which has been a big...
1,379
Please take a look at my averaging Ladder. I only want the average of the last 10 values. Convoluted or straight forward? Is this the way you do...
2,553
Hi there, I have an expression N24:[N24:0], which places a value in data file N24, these values are indexed with reference to N24:0 according to...
3,006
The PLC code calculates oil flow rate and outputs it on D420. It is represented on the HMI as a vertical bar. Problem is that the operator says...
33
4,995
Hello, I am working with a laser encoder that is providing the speed of a fiber strand to our AB 1756-L61 PLC. In order to calculate the amount...
3,173