Banner DX-80 radios - flex power DI's can not handle a dry contact switch closure?

danw

Lifetime Supporting Member
Join Date
Oct 2004
Location
midwest, USA
Posts
3,427
I've used Banner for RTD's, thermocouples and 4-20's but not for discretes.

I called the factory to find out whether either PNP or NPN wiring would draw battery power with a dry contact level switch wired to a DI on a battery powered 'flex power' node radio (Performance P5, 18142) and was told that the radios can not handle dry contact inputs.

Is that really true? The wiring drawings use classic switches:


P5-DI-wiring.jpg
 
Huh? Must be some misunderstanding.

We have one of this and we use one of the input wired to a limit as a closure temper switch. It's just a dry contact and their diagram also shows the same.
 

Similar Topics

Hello everyone, I need your help to guide me how to make this screen appear when the alarm is present, I have already configured its size and the...
Replies
5
Views
145
I'm using FactoryTalk ME version 13. I have an alarm banner that is an on top display. Whenever there is an alarm this banner becomes visible to...
Replies
3
Views
904
This is an issue that I noticed we have had recently on this keypad HMI, an alarm will come up and it can be acknowledged by a fault reset button...
Replies
0
Views
560
Has anyone here on the Forum used the new Banner DXMR90R-4K IOLink Master device with an S7-1500 or similar ProfiNet controller ? Banner has been...
Replies
1
Views
910
Banner , Sick , etc. Slot on Fork Sensors . Do they make them wider than 8.66 " ? Good Morning , I have product that is coming down the...
Replies
3
Views
1,031
Back
Top Bottom