Hello guys,

its my first post on this forum. I am intermediate user but just started working with actual hardware PLC. i have s7-315 siemens CPU. and i have problem about addressing to I/O in my program.

Please explain me everything related to how to address that exact pin on input or output. For example i have DI 32 *DC card. And over it there are 40 screws or slots. i understood top 2 is for supplied voltage and bottom 2 is for ground. but how to address them when i want to use in my program S7.

while hardware in my s7 shows something different. its showing I 8....11. what does that mean. and what if i want to access first pin of this Input module.

damnnn
 
Short answer to get you started: Siemens PLC addressing works in bytes. A byte is 8 bits. So, your 32-channel input card has 4 bytes.

You can define what bytes to use for each card in the hardware configuration. If you configure that 32 bit input card to use bytes 0-3, then your addresses will be:

I0.0
I0.1
I0.2
...
...
I0.7
I1.1
I1.2
...
...
I1.7
I2.0
I2.1
...
...
I2.7
I3.0
I3.1
...
...
I3.7

You could equally configure them to be bytes 29-32, and then you would have I29.0 through I32.7. Completely up to you. Just make sure there's a logical pattern for ease of troubleshooting.

As JRW mentioned, some screenshots of your hardware configuration will make it easier for us to help :)

EDIT: just noticed your comment about hardware configuration showing 8-11. If you mean what I think you mean, then that means that the card has been configured to use input bytes 8 through 11. So your first 8 inputs are I8.0 through I8.7, and your last 8 inputs are I11.0 through I11.7.
 

Similar Topics

Hi all, I have a noob question regarding data handling from sensors. I understand configurations and I/O mapping sensor input/output variables...
Replies
2
Views
227
Hello I am new here and new to PLC's, I wrote this program for a class that I am taking and my local tech school. The description is switch 7 will...
Replies
0
Views
422
Hello I am new here and new to PLC's, I wrote this program for a class that I am taking and my local tech school. The description is switch 7 will...
Replies
10
Views
1,994
I’m a bit stuck on HMI (KTP-1200) programming… See the picture attached. The PASS or FAIL box should only appear when the toggle switch is...
Replies
7
Views
1,091
Hey Programmers, Heres todays puzzle I was trying to solve... I have a Modbus TCP network with two Modicon M221 controllers live on my work bench...
Replies
0
Views
482
Back
Top Bottom