Beckhoff Ethercat Problem!
klikopc
Jun 2009
Ptuj
64
Hi!
I use a PC with Beckhoff Twincat as the control system that is connected via a ethernet cable to a EtherCat unit with 2 EL1008(8 Inputs) units, 2 EL2008(8 outputs) units and a EL3203(temperature sensor).
Everytime the Ethercat power supply goes(PC still has power) down or someone disconnects/reconnects the ethernet cable, Twincat can't reastablish the connection with the EtherCat unit. The program is still running, but without the connection to EtherCat.
I have to restart the Twincat System runtime to get the connection back.
Can anyone tell me if it is possible to detect the connection loss within the Twincat program itself or some other way to solve this?
Matic
Sounds like the ethercat master is not returning to OP state - you can request OP state using FB_EcReqMasterState in the EtherCAT library, or have a dig around the EtherCAT configuration in System Manager - it can probably do this automatically if configured.
Roger
At my current job we have a relatively new system that has an Allen Bradley PLC as the main controller with some local I/O, but a lot of remote...
2,710
Hello, I have a Beckhoff TwinCAT system with local I/O and a remote EtherCat Box I/O. The Beckhoff TwinCAT has failed and needs replacement. Is...
1,721
Hello, I have several VFD's that communicate Ethernet/IP, and need to integrate these drives to an existing Beckhoff EtherCAT network so that...
3,458
I am tying to connect a PILZ pnoz m1p plc with a Beckhoff CX9020 plc true Ethercat. I have connected a PNOZ mc2.1p ethercat module to the PILZ...
2,408
Hi guys anyone had this before? Latest AX5103-xxxx-0011 xml files from Beckhoff's site added in the device repository using ABB's Automation...
3,146