beijer exter T70 Modbus comms

I have done a bit more fiddling and found that the locations that the HMI is requesting are definetely double what it should be looking for. So where I ask to display 40004 it displays 40008, where I ask for 40006 I get 40012 etc etc. It still writes everything to the right spot from the same box that has the incorrect display...
 
I have used Modbus on Exter Units successfully many times (but never with Splat).

A couple of questions to narrow things down here:
  • Is the Exter panel a Modbus Master or Slave?
  • Which Flavor of Modbus are you using? ASCII, RTU, TCP
  • Are you using any index registers?
  • Does the firmware version in the Information Designer Software match the actual firmware on the T70 (Check Menu choices Project/Properties/Operatot Terminal)
  • Do you have the latest version of the modbus driver? (Menu Choice File/Update Driver/From Internet)
It could also be a bug but you should ckeck all of the above.
 

Similar Topics

Hi, I'm currently having an issue with a Beijer T70 HMI. We have 2 HMIs talking to a Yaskawa motion controller via modbus over ethernet. The...
Replies
0
Views
582
Spent the best part of the day trying to figure a problem with the Beijer Exter series no protocol mode. I got it sussed and so thought I would...
Replies
0
Views
3,315
Does the Beijer Exter support PID blocks using the CLX (compactlogix)driver & using the L5K import . CLX Ver 4.15
Replies
2
Views
1,831
Hi Is there anybody on this forum who worked on Exter Touch Screens from Beijer Electronics. More precisely with the controller data exchange...
Replies
13
Views
5,929
Is it possible to exchange data between compact logix and Moore(Siemens) DCS through Exter HMI Screen? I am using Compact Logix L35E processor and...
Replies
0
Views
6,034
Back
Top Bottom