I've got 6 identical regenerative vacuum blowers powered by 6 identical drives in 3 identical panels all fed from the same 1 main building feed doing the same thing, robot end of arm vacuum tools in pairs, two blowers per tool.
I've also got about 20 randomly timed trips for overvoltage and ground faults between them and I'm hoping maybe someone will have ran into a similar issue and has ideas or advice.
More details:
-Powerflex525 480v 15HP 25B-D024N104
-2 Pole 3550 rpm 11kW motor direct drive to regenerative blower
-Ethernet/IP controlled from 5069-L320ERS2 PLC.
-1.00s Accel (unachievable but need blowers to start as fast as possible)
-25.00s decel but Stop mode is Coast,CF so it doesn't mean anything.
-Run static 40Hz(from PLC), start signal(from PLC) is singular so they both start and stop together
-5 minute timeout in PLC shuts them down to save energy, startup can be immediate, during coast down, or anytime after being stopped due to process variability
-Flying restart is enabled and Flying Restart Current Limit is 200%. Was having significantly more issues with Overvoltage trips prior setting these this way.
-Time between trips on any one drive is between 100 and 1000 hours which has made this a bear to debug.
-Every time I've ever seen a trip was when a pair of blowers tried to start, but I have not seen every trip to know if this is truly correct.
-Every time I've seen this happen, they are able to reset and start fine the second time.
Seems odd to me to get a bus overvoltage fault when trying to start a motor. I suspect it has something to do with the drives trying to 'catch' the spinning blower as its coasting down to spin it back up because giving it more flying restart torque helped reduce the frequency of these faults. Watching the Output Frequency when it starts regardless of success or failure is interesting, hz flashes up around 58-60 for a split second, then down to the normal 0-40hz ramp. You can also see on the attached doc that when drives fault the HZ is always in the 55-60hz range which these never spin at. Any ideas or advice is greatly appreciated.
First plan of action is to extend accel ramp a bit since process isn't running fast enough to notice it, yet, and see if that helps. Braking resistors are another thought given the fault, but what causes this on startup?
I've also got about 20 randomly timed trips for overvoltage and ground faults between them and I'm hoping maybe someone will have ran into a similar issue and has ideas or advice.
More details:
-Powerflex525 480v 15HP 25B-D024N104
-2 Pole 3550 rpm 11kW motor direct drive to regenerative blower
-Ethernet/IP controlled from 5069-L320ERS2 PLC.
-1.00s Accel (unachievable but need blowers to start as fast as possible)
-25.00s decel but Stop mode is Coast,CF so it doesn't mean anything.
-Run static 40Hz(from PLC), start signal(from PLC) is singular so they both start and stop together
-5 minute timeout in PLC shuts them down to save energy, startup can be immediate, during coast down, or anytime after being stopped due to process variability
-Flying restart is enabled and Flying Restart Current Limit is 200%. Was having significantly more issues with Overvoltage trips prior setting these this way.
-Time between trips on any one drive is between 100 and 1000 hours which has made this a bear to debug.
-Every time I've ever seen a trip was when a pair of blowers tried to start, but I have not seen every trip to know if this is truly correct.
-Every time I've seen this happen, they are able to reset and start fine the second time.
Seems odd to me to get a bus overvoltage fault when trying to start a motor. I suspect it has something to do with the drives trying to 'catch' the spinning blower as its coasting down to spin it back up because giving it more flying restart torque helped reduce the frequency of these faults. Watching the Output Frequency when it starts regardless of success or failure is interesting, hz flashes up around 58-60 for a split second, then down to the normal 0-40hz ramp. You can also see on the attached doc that when drives fault the HZ is always in the 55-60hz range which these never spin at. Any ideas or advice is greatly appreciated.
First plan of action is to extend accel ramp a bit since process isn't running fast enough to notice it, yet, and see if that helps. Braking resistors are another thought given the fault, but what causes this on startup?