Breaking Capacity.
Riche Robledo
May 2011
Dubai,UAE
36
Good day to all... :unsure:
Please help me to know the breaking capacity of MCB circuit breaker?
Example.. 1000 ampere MCB circuit breaker..
are there any computations to get that breaking capacity?
any idea you may help me to clear my problem...
Respectfully yours.
RR
It is one of the data that must be informed by the manufacturer.
The short-circuit breaking capacity is typically printed on the circuit breaker on the front or the side. Or find the data sheet for the circuit breaker in question.
sir Jesper..
I dont have data manufacturer for that breaker..i want to know only the short circuit breaking capacity for 1000 amps MCB circuit breaker? is it more than 1000 amps,exactly 1000 amps, or below 1000 amps the circuit breaker will trip?
thanks...
RR
Riche Robledo.
"Breaking capacity" is how much current the circuit breaker can interrupt. This value is normally much higher than the rated value for the breaker. It has to be.
When the breaker will trip is a totally different question.
For knowing when the circuit breaker will trip, then you will need the tripping characteristic for the breaker in question.
Both breaking capacity and tripping characteristics cannot be derived just from knowing the rated current value. You need the exact data from the exact breaker type you intend to use.
Hello, I am working on a SCADA system using Wonderware Intouch 2014 R2 and have a small glitch with the historical trend feature. Every time I...
2,860
I know tabview is not a PLC but I also know that some of you use LabView for a HMI and data acquisition. We have at a !@#$% if a time with...
4,328
I was listening to the radio today and a discussion about Simulation Hypothesis came on and it was quite intriguing and actually entertaining. I...
2,054
Since I had to relocate, I've been working in new construction as an electrician, however my boss is definitely open to letting me take on...
2,956
Hello All, First of all I am using an AB Logix 5571 revision 30. I am trying to use a FBC to tell me which slave is unplugged in order. The...
2,384