Bus-Off DeviceNet Status reading from PLC

golftmd13

Member
Join Date
Feb 2018
Location
Missouri
Posts
9
Does anyone know if its possible to pull a Bus-Off status from a DeviceNet card on a PLC that can be displayed to an HMI screen that the fault has occurred. If so how is it found? I found in the controller tags that you can look at the status on a node level but I'm looking for a level over the whole card/module.
 
What DeviceNet module in what PLC ?

All the Logix-family DeviceNet bridges include a Local:S:ScannerStatus tag that should tell you if the port is in a bus-off condition.
 