BX9000 Communications With RSLogix 5000

Portlyjent

Member
Join Date
Dec 2011
Location
Colorado
Posts
3
Hi, Bit new here but have a pressing issue. I am trying to establish communications with a Beckhoff BX9000 through ethernet to a Logix5000 rack containing an ENBT/A and a 5561 processor. I only need to read data from the Beckhoff and so far there doesn't seem to be a method to bridge the TwinCat ADS/ TCP Modbus to RSLogix's OPC/ TCP IP any suggestions?
 
Since your ControlLogix doesn't implement either of the Ethernet-based network protocols that the Beckhoff I/O base does, you need some sort of interface or gateway.

The simplest and fastest would be a MVI56-MNET module from Prosoft, to read data using Modbus/TCP from the Beckhoff device.

There are several standalone gateway devices that will also do this, from Prosoft or HMS Fieldbus or even Digi.
 

Similar Topics

Hi, What is the trick (if there is one) to accessing a Bx9000 over a VPN? I know there is something finicky with network config when even local...
Replies
6
Views
2,102
Hi all, I have a machine with a Beckhoff BX9000 cpu that looses the source code every few days in the production. The name and the network...
Replies
0
Views
1,646
hi all, i have a Beckhoff BX9000 CPU which is magically reset to factory settings in every once in a while. Do you have any idea what could cause...
Replies
0
Views
1,580
I am newbie in using the Twincat software. I have tried to connect between Beckhoff BX9000 and Twincat. But I was not successful. In the Twincat...
Replies
3
Views
5,667
Hi all, I want to connect a BX9000 with ethernet to my laptop. But the BX9000 has bad pixels so I can't read the IP.. I'm a newbie but how can I...
Replies
2
Views
2,427
Back
Top Bottom