hello ...
i facing a problem with I/O unit for omron c200he..whereby the output bit
can be triigger ON..but i cant the external relay on ..
i had replace with new unit as well..also i had check present of 24vdc
using ID216..pin no 9 connect to 24vdc and pin no 1- i connect to 0VDC..
had i miss anything on this ..
attach is the drawing ....
..on motor stater control ..all no 2 would OVDC from control panel
NO 1 is output from PLC module 24vdc ..
also attach drawing PLC module output
the drawing not clear,
but the OD215 transistor go to relay then to PLC terminal positve line
check you wiring again
Can you PDF the two drawings you have please
the image is too small for these old eyes.
Have you tried to force the output ON
I note you said ID216 - this is an INPUT card
Please confirm
hello
yes i had try to force on the output but force the input and it show the bit is on .and check ed the LED also light up ..but dunn why cant trigger my relay 24vdc..
i try rescan the pic ..hopely some1 could help me ..even i try change to new
output still..btw is it not input it output my mistake on that
..yes i m using the 24vdc as return to output.as same drawing ..
1 more question ...what is the following bit adress would be for chn output number 7 on output 0D215 ..example the terminal A i set from 170.00 to 170.08
than next terminal is connector B i set 171.00 to 171.00...continue for terminal connector A again as 172.00 to 172.08 and follow by B as 173.00 to 173.08..is this correct what i did
:confused::confused:..kinda new using CX software..can say learning still using window base
hai all thanks for all the info ...
finally had settle the problem...change to new output module and try it work ..than swap back to the old and try again but not work..wat i found is 1 of the output bit is not working
the output cards are limited to extremely low output currents.
look carefully at what you are switching
If the output card is a relay card it can carry a maximum of 3 amps resistive load.
If you are switching AC then you must use an interposing relay.
this is usually industry best practice
Hi! I am having a problem with the C200HE. It has a SRM21-V1 communication module with SRT1-ID08 remote input module. I think the protocol used...
1,656
Hi, I wish to connect to the OMRON C200HE PLC via its peripheral port, using omron's RS-232 interface adaptor. I have no ethernet module for...
5,487
First to say... I'm a systems manager with wide interest in PLC's. But I'm New. We have a Symac C200He CPU42PLC in the house. Last sunday we have...
1,560
Hello..all i have 1 project to upgrade C200HE to CQM1 omron plc ..need expert suggestion been told to change old model to CQM! model ..which i...
3,748
hello all i would like to seek some advice and also some guide for my problem as below . 1st.. lately i been having problem with 1 plc (cimon)...
1,686