Calculating KWh from KW
Marc_U
Sep 2006
Cumbria
193
We have a few sites that have Redlion G3 HMIs which are monitoring Hydro-electric generation sites.
The HMIs have access to the generator kW reading (via modbus), but we would like to also able to calculate how many kWh (kW hours) have been generated.
Any suggestions?
o_Oo_O:confused:o_Oo_O
Uhhh... Totalize the readings up over some time interval?
For example, take a reading every minute, divide it by 60, and add it to an accumulator. The accumulated value represents kWh.
If the kW is varying considerably during the period of one minute the reading will be inaccurate. Better to do it every second on varying load.
Lot easier to buy a kWh pulser from Crompton Instruments to be honest.
I would go further than Bob and suggest that even 1 second updates will not be accurate unless the load is stable and linear. If you are already using Modbus then I would look at a multifunction energy meter like the Schneider PM710 which will give all of the information you are likely to need and does not cost too much.
Strangely enough my favourite power monitors come from Cromnpton Instrumenst in the UK Andy.
Love em - real easy on Modbus RTU - very accurate too.
Also use the blind ones for 4-20ma outputs - up to 4 per unit.
Thanks for the suggestions.
Precision is not too critical, as it is intended more as an indication.
Like a few of you have said, for the critical precision kWh (where loss of revenue is involved), then if possible I would use a Modbus link to a calibrated instrument.
Thanks again.
This application has a motor with encoder feedback that drives a linear actuator that moves in/out, and is at roughly 45 degs from horiz. As the...
19
1,398
I need to keep a running pass/fail yield of the previous 5,000 parts produced. I have used this formula before to calculate average: AvgValue =...
2,188
Does anyone know how to calculate the savings from now needing to run an air compressor all day? Basically I have a design that replaced 6 * 1"...
26
4,903
I would like to refer to this document of which I used some data ...
1,490
Seems like this should be a simple thing but I’m struggling with it. The basis is that I am trying to detect if a linear assembly is stopped or...
3,125