I buy New CPU 1769-L32E, But When I try to download Program to CPU,
I can not download because there is error
I don't understand about this Error.
Anyone can suggest me to troubleshoot this problem Error.
Thank everybody
alpine
What RSLogix 5000 Revision and Release are you using?
What CPU Firmware Revision and Release is running on the CompactLogix?
I use RSLogix 5000 Version 20.00
Dear dmargineau
I use RSLogix 5000 Version 20.00 and
I use Firmware Version 20.13 running on CPU 1769-L32E
What I am looking for is the software Release Version.(RSLogix 5000, Toolbar-Help/About RSLogix 5000-> CPRx, SRy; x=? y=?)
From Allen Bradley Knowledgebase
Access Level: TechConnect
Date Created: 03/06/2012 11:07 AM
Last Updated: 01/14/2013 08:18 AM
Question
What does the RSLogix 5000 download error "Attribute value not settable" mean?
Answer
Verify that the RSLogix 5000 software is an actual released version.
In one case, customer had Beta RSLogix 5000 software, trying to download a program to a 1769-L32E processor with released V20 firmware in it.
When the program was converted to a released version of RSLogix 5000 V20, the program downloaded to the 1769-L32E just fine.
I should use Firmware V20 release CRP9 SR4
Dear dmargineau and MATT116
I think when I use RSLogix 5000 V20 CPR9 SR4
Therefore, I should use Firmware V20 release CRP9 SR4 same as
release version of RSLogix 5000 (CPR9 and SR4)
I think this is correct ?
I will try to download firmware V 20.012 to CPU
Dear MATT116
Now, I try to download firmware V 20.012 to CPU and I will tell the result to you
I have already downloaded Firmware V20.012 to CPU
Dear MATT116
I have already downloaded Firmware V20.012 to CPU, But I can not download program to CPU. the same problem remains
There is a note regarding the Error you are experiencing within the RSLogix 5000 Rev.20 Release Notes (http://netstorage.rockwellautomatio...n=1363964725_c2af6edc081223db593957e82f6b8d74
however, this is relatied to trying to use RSL5K Rev.19 with Rev.20 CPUs.
You might have to downgrade the L-32E to Rev.19...:(
Do you have RSLogix 5000 Rev.19?
1969-L32Es are "maxed out" with firmware revision 20; they are being replaced with the new generation 5730 CompactLogix CPUs; I have personally experienced issues with running Revision 20 firmware on "old" Logix CPUs and I believe some Forum members ran into something similar; "downgrading" back to 19 seems to be the proper software/hardware functionality issues mitigation.
I use Windows 7 , 64 bit, Now, I used Firmware V16 finish, This Work !
I can download and run program finish.
Thank you everyone
see you next time,
alpine
Glad to hear that.
You might want to go to 19 though; you are "losing" plenty of functionality features when running Rev.16 firmware on a CPU capable of 19.
Hi I am having a problem with flash download to a new compact logix PLC. I got on line to the new PLC using a serial cable. RSlinx could see the...
6,856
Hi everyone: I went to AB.com, found only firmware, no EDs file showing up. i took a pix of device properties of RSLinx. Thanks
145
Hi All, I was making some offline changes to one of our machines PLCs (1769 L33-ERMS), and I noticed that downloading to the PLC took a lot...
1,232
Due to a UCP power failure my 1769-L35E CPU has been inadvertently killed during the firmware update process. (don't laugh - it's not funny)...
2,907
I am using RSLgix 20.0 and RSLinx 2.59 When i try to connect to L16 controller i get the error "Attribute value not settable". In offline mode the...
1,409