Can't read analog card in logix designer
gsingle
Mar 2019
iowa
Hello everyone,
My transmitter is reading currently in control panel, showing 14.9mA. I configure new tag in studio5000(logix Designer), but it is showing me 0 value.
I don't know if I miss something.
The card is 1746-NI16, controller is 1756-L74 controllogix 5570
and logix designer V28.02
Please help me out, I am new to this software.
Thanks in Advance.
So, lets start at the beginning.
In your L74 controller, if you go to controller tags, and browse to the IO module you mentioned. You should see raw counts for each channel, do you have a value in the channel that your transmitter is connected to?
Has the channel been configured? Each Channel has an output word. The bits in this word determine how the channel functions.
Assuming you have the card set up for a 4-20mA signal, you should see a number between 3277 and 16384
Raw value is showing me 49360. It has Input type0,1. Data format 0,1,2. Calibration0,1,2. Filter frequency 0,1,2. and channel enable.
I click on Channel enable, Input Type1, data format 0,1 and filter frequency 2
It is showing me 11000000 1101XXXX with raw value 49360
Hi everybody Does anybody have experience with the Analog input card 1746-N18? Cannot get the last 4 inputs (4-7) to work like the first 4 (0-3)...
2,982
Hello, I'm working with a 1747-NI4 analog input module (for the first time) on a SLC503 processor. I noticed in the IO configuration within...
4,778
Hi, I need some help reading the value of Channel 0 of a 1769-IF4 card. The analog card is in slot 1. So the Input value should be...
3,951
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
256
Hi all, I want to catch min piks of an analog signal when digital signal is on(pls see the attached oscillogram). My hardware is 5069-L306ER CPU...
1,015