Can't set IP on EN2T
MartyMaucher
May 2014
Pensacola
91
Using 1756-EN2T Ethernet card. Got BOOTP running to set IP to 192.168.1.2. BOOTP sees the MAC address, but never sets the IP on the EN2T card. Connected through Stratix 2500 lightly managed switch.
I also tried connecting by USB with RS Linx Classic, but it doesn't see the card, either. The card scrolls BOOTP (MAC address) and IP Address/Mask/Gateway Invalid.
Any ideas?
Make sure that your "network settings" on the BOOTP/DHCP Server utility are configured so that the Default Gateway and Subnet Mask are set up so that the Gateway address is on the same network as the IP address.
Very typical:
IP: 192.168.1.2
Subnet Mask: 255.255.255.0
Default Gateway: 192.168.1.1
If the default gateway was, for example, "192.168.4.1" then it would not be on the same subnet as the IP, and would be rejected by the module.
The server/laptop is static at 192.168.1.1. I set the Gateway to the same. I can ping the display at 192.168.1.3 (through the same network switch).
When selecting "Enable BOOTP", it pauses while it says "Attempting to connect to <MAC address>" and times out. It seems like DHCP protocol is not getting through the Stratix 2500 network switch, but I also tried it with a regular NetGear switch with the same results.
RSLinx is v4.11
Double-check, triple-check, and then quadruple-check the Network Settings in the BOOTP/DHCP utility.
What you are describing is exactly what I see when I make a typo in the Network Settings.
Ohhhh..... the Mask and Gateway setting IN BOOTP Tools, Network Settings (not laptop network).
Got it set, And it's working.
Thanks so much, Ken.
I should have been more clear: the Subnet Mask and the Default Gateway are settings you make in the BOOTP/DHCP Server utility itself, not the settings for your own PC's network interface card.
Main Menu -> Tools -> Network Settings
So I have code to read the IP address of a 1756-EN2T with a MSG block - Get Single Attribute. Does anyone know where to find the MSG block...
1,154
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
34
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
19
337
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
104
I was loading a program onto an XE1e2 PLC and it got stuck on these two windows and won't progress. It won't let me connect from the PC to reload...
87