Cascade loop in manual mode
learner
Apr 2007
British Columbia
81
Hi there,
I would like to know how I can set the output of my PID cascade loop to zero as soon as it goes to manual. That's just for the safety. Also I would like to be able to give it different setpoint in manual mode and run it. The problem is that if I tell it to set it's output to zero in manual mode then I wouldn't be able to give it different set points and operate it in manual mode.
Regards
This is a simplistic way of doing it
Post the output of the PID into a register (say R1). Use this register to post the value to the analog output.
An auto contact should be in the rung before the PID instruction
Now have your mnanual mode below the auto PID, and use HMI values to write into the register R1 using a move instruction.
Depending on your PLC many have Manual mode built into them
Cheers
Just to check my sanity even though I think I found the solution. So, for this loop with long lag time we got 2 PID loops with the Outer Loop...
1,179
Hello!! I'm working on a project that requires a Cascaded PID Loop to control solution temperature in a tank with a water jacket. The tank has...
2,429
Hello all, Sorry if my doubt is too basic. I have a material heater. Cold material enters the heater and hot material comes out (too obvious? :D)...
23
9,296
Dear all I would like to ask you for help in solving one algorithm, because I never worked with cascade PID. I have to realize heating valve...
8,358
I ask you answer if you know precisely what PID loop update time in a Rockwell processor is and if you are experienced with cascade loops. Thank...
5,782