Cascading PID Loop Tuning

Chado613

Member
Join Date
Mar 2005
Location
Kingston
Posts
79
Just curious to see what are some of the more favorable methods?

I have never used one before and will be commissioning one in the near future.

Is it better to tune the master first? slave first?
Can autotune be used? (Programming with RSlogix 5000)
Any feedback would be greatly appreciated.

Thanks
 
Hi Chado,

Check out this link, it explains a procedure for tuning a Cascade loop:
http://www.controlguru.com/2007/090207.html.

You will want to tune your Inner / Secondary / Slave loop first, this is because the inner loop is your "early warning" and any disturbances in inner loop impact the process variable of the outer loop.

If you tune your outer loop first, then it will not be tuned correctly after you tune your inner loop.

If you tune one loop at a time you can use software. I actually have Control Station's LoopPro Tuner and you can use this to look at both Manual mode / Open loop and Setpoint driven data, although you can manually calculate tuning parameters in Open Loop. However you have to do each loop one at a time (two bump tests are required) and not both at the same time.

I haven't used Autotune however.

At the very least check out the link and follow the procedure there. Elsewhere on the site there are IMC derived tuning correlations you can use to calculate tuning parameters. Here is the page for Non-Integrating processes (90% of the time). Here is the link for Integrating processes.
 

Similar Topics

I need a little help tuning this system. I am using a SLC 5/05 processor. What I have is a paint booth that requires me to be able to control the...
Replies
12
Views
4,628
I am wondering if its a good idea to cascade pid loops. For example If I want to control two variables Current and Voltage. If i can feed output...
Replies
4
Views
2,783
Can someone help me understand cascading PID loops? We are controling a steam valve through a heat exchanger this way, and I am having trouble...
Replies
2
Views
3,003
Ok! I could really use some help getting off the ground with this one. I have in the past programmed cascading PID's but for some reason I...
Replies
0
Views
4,337
Good Evening , I have a Conveyor system that requires Speed Cascading from one conveyor to another. Meaning that if one conveyor speed is...