Hi,

I have a flow meter which needs to be connected to our SCADA via GPRS/GSM/4G or any cellular type RTU's If any one have an idea please share

Sandy
 
List the model of the flow meter.

If it has Modbus TCP it will be easy (if your SCADA has Modbus TCP drivers, which most do).

If it is Modbus RTU you can put in an RTU to TCP converter. If only Pulse or 4-20ma/0-10V you will need a small PLC in the middle.
 
3g and 4g connect the remote site to the Internet.

Thinking about modems in now days, on everything moves through the Internet, is an outdated concept
 
Hi,

Since we are thinking about 3g/4g private ip is not available for mobile data in our area..please suggest if you have some idea
 
You do not need a static or public IP at the remote site to establish a VPN connection as a client. A cheap contract, a cheap SIM card with only data transmission should work, no need to ask for a unique or static IP.

On the other hand, the internet connection in the plant where the SCADA is needs to have a static and public IP but this is easier to achieve for a cable or ADSL connection.

If you still don't understand it yet, consult a network administrator.

It is the same system that many people currently use to work from home or from remote sites.
 
Last edited:

Similar Topics

Hi all, I have a client that has a water tank with a loop powered level sensor; the 4-20mA loop goes through a telephone line, half a mile away...
Replies
26
Views
6,987
Hello, We are looking at setting up some machines in another country where internet is not available. We could use some cellular service where...
Replies
1
Views
1,294
I'm using ICX HWC35 cellular gateway with Allen Bradley 1769 L33ER PLC for messaging purpose Already upload the AOI instruction to the project...
Replies
3
Views
4,400
Hello everyone, I connected icx35hwc to 1769 l33er PLC And recieve messages when triggering "ICX35.CONTROL.Read_SMS "tag in control tag section...
Replies
1
Views
1,626
it is possible to transfer live data from micro 820 PLC to Compactlogix 1769 L33er using ICX35 HWC gateway. If possible how it's done. Note using...
Replies
0
Views
1,000
Back
Top Bottom