ICX HWC35 cellular gateway message recieving problem

anirudhgk7

Member
Join Date
Feb 2019
Location
Kerala
Posts
42
I'm using ICX HWC35 cellular gateway with Allen Bradley 1769 L33ER PLC for messaging purpose
Already upload the AOI instruction to the project and recieve messages when triggering. "ICX35.CONTROL.Read_SMS". Tag. (It's a Boolean tag.)
How this tag trigger repeatedly for every 30 seconds to receiving messages. In studio 5000.
 
Run a 30 seconds auto resetable timer, every time the timer completes 30 seconds it triggers your AOI.
You can also use seconds from real time clock and trigger your AOI every time seconds are 0 or 30.
 