I would agree with val_99, and suggest that you have the burner control relay control both of the valves, and simply let the PLC apply a command to the burner control relay...
The burner control relay is much more than a relay. It will include a flame monitor input and possibly an airflow proving input as well as time limits for flame proving and will be certified (if installed according to requirements) to handle the job.
I'm with OkiePC and val_99 - the point is that if you change anything about a control system, especially one that has been designed some years ago, you then become responsible for the design of that system: unless of course you are just replacing a fuse or swapping one relay for a like device.
Once you start adding a PLC YOU are LEGALLY responsible for the system .
If you want to cover your back, then any design you do MUST be checked and verified by a competent engineer with experience in the field that applies, in this case burner applications
Suitable solution would either be a safety PLC (S7-300F) with the right safety functions (eg burner monitoring) or use a standard PLC with a burner control relay (Honeywell, Landis & Staefa, etc)
jdbrandt's comment about hard wired timers is good, and we've used these for functions such as watch-dog, but not for failsafe controls like burners