CIP Communication between Schneider M580 and L32E Compact Logix
Engrlife
Aug 2017
British Columbia
41
I am trying to setup communications between an m580 and a compactlogix plc. I have confirmed my set up on schneider side is correct and now I am trying to troubleshoot the Allen Bradley side. The error I am getting is Configuration data size is too short. This is on a message block, CIP generic, Service type Get Attribute single, instance 101, class 4, attribute 3. I have added the 4 extra bytes required to my destination structure, and I have also tried using a significantly oversized array of 50bytes (I am reading 18) always getting this error.
Solved: I got on tech support with AB and future reference to anyone doing this. All the parameters I listed were correct for the described communication from eip slave 1 on the m580. The thing I was missing is on the Logix side you need to set up the cip block as custom and put a source tag in that matches the eip data structure from the m580. Then fill in the rest of the info (Instance class attribute service code which will be e for get attribute single) then the source tag will be greyed out but still used.
Having an issue with network timing out when trying to use CIP generic on a Micrologix 1100 B. I’m trying to read flow and totalizer information...
19
5,045
Hello, I am very new to PLC programing, I am able to program very basic system (stand alone machines) and HMI, but that about it ... I now need...
1,879
Hello, I need to establish a CIP safety communication to a KUKA KRC4 robot. The KUKA has the IP 192.168.11.53. I already established a standard...
10,282
Hi there, We had a Compactlogix CPU failure few days back in one of our compressor station, it was series-A 1769-L35E processor with v15.xx...
5,348
Hi everyone, I am having trouble setting up communication between wonderware intouch 2014 and Controllogix L55 rev 11 processor using DASABCIP...
3,835