DASABCIP 5.0 with Controllogix L55 M13 redundant processor communication issue
nilx007
Jul 2015
Pittsburgh
Hi everyone,
I am having trouble setting up communication between wonderware intouch 2014 and Controllogix L55 rev 11 processor using DASABCIP 5.0
I tested the application in house and communicated fine with the L72 processor Rev 19.
Now I'm on site, trying to set communication and its giving trouble. I checked the diagnostic and its showing client group error (red). Log viewer has error code 0318: Link address to self invalid.
any help would be greatly appreciated.
Thanks,
Neil
The hardware configuration is as follows.
chassis#1, slot 0=processor and slot 1=CNB module.
chassis#2, slot 0=redundant processor and slot 1=CNB module.
Chassis#3, slot 0=CNB module & Slot 9 = ENBT module.
HMI is connected to ENBT module via ethernet switch
The ABCIP hierarchy I configured in DA server is as follows
CIP_PORT >> parameters: max qued msg =4
ENB_CLX >> Parameter: host name: 100.100.100.10 (IP address of PLC), connect time out 2000 ms
Backplane_CLX >>
CNB_CLX >> parameter: slot number = 0
PORT_CN >> parameter: channel number=channel A, controlnet address=3
CNB_PORT_CLX >> Parameter: slot number= 1, channel number= channel A, Controlnet address=1
Backplane_CLX >>
LOGIX5000_CLX>> Parameter: slot number=0, reply timeout=15, max CIP conn =4, optimization= no optimization, Tag database= auto load tag checked
device group is = PT added in logix5000_CLX parameter
the same is access and topic name in HMI application with suitlink protocol
oh well the problem is resolved. I was getting error due to mismatch in the hierarchy parameter i configured in DA server and actual node addressing in Controllogix.
the chassis # 3 which has ENBT card was actually configured as node 1 and primary processor chassis as node 2 and secondary processor chassis as node 3
simply changing the parameter of PORT_CN & CNB_PORT_CLX as below resolved the issue and its running like a champ.
PORT_CN >> parameter: channel number=channel A, controlnet address=1
CNB_PORT_CLX >> Parameter: slot number= 1, channel number= channel A, Controlnet address=2
Thanks,
Neil
Hi guys, I'm working with my AB ControlLogix PLCs and my task today has been trying to get the PLC to talk to my Intouch HMI. I started out with...
3,205
Hi Chaps,Could anyone explain how to configure DASABCIP in SMC to communicate with control Logix controller in the remote chassis. My L75 is...
4,271
First, hello to everyone and thank you for your time. My problem is as follows: 1756-L73 v19.13 communicating via DASABCIP.4 to WonderWare...
4,091
I am curious to see how many people have tried ControlLogix firmware version 18 with Wonderware's DASABCIP? We currently have version 16 and 17...
2,775
Hi guys, I'm working on a Water treament plant application in wonderware 9.5 and using DASABCIP v4.0 as the server. It is connected to a...
29
21,399