Hello All,

I am running Citect SCADA 2018 R2 and trying to connect to a AB ControlLogix L81E. I have configured the board, port and IO device according to the Citect help function and cannot seem to get citect to communicate with the PLC. I can ping the ethernet card from my computer and have configured it such that it points to 192.168.0.26/0. CPU is in slot 0. I have tried updating to the latest driver and that has not fixed the issue either. We are routing through a Siemens RuggedCom RSG2100 switch but as stated before I can ping so I don't believe that is an issue. Is there extra configuration needed because I am routing through a switch? Could it be that there is extra configuration needed on top of the latest driver install? Everytime I run up the runtime i get the #COM error seen in the attached images. Anything you you guys can think of would be greatly appreciated.

Thank you

Board.PNG comms issue.PNG IODevice.PNG port.PNG Tag Addressing.PNG
 
Hello All,

I am running Citect SCADA 2018 R2 and trying to connect to a AB ControlLogix L81E. I have configured the board, port and IO device according to the Citect help function and cannot seem to get citect to communicate with the PLC. I can ping the ethernet card from my computer and have configured it such that it points to 192.168.0.26/0. CPU is in slot 0. I have tried updating to the latest driver and that has not fixed the issue either. We are routing through a Siemens RuggedCom RSG2100 switch but as stated before I can ping so I don't believe that is an issue. Is there extra configuration needed because I am routing through a switch? Could it be that there is extra configuration needed on top of the latest driver install? Everytime I run up the runtime i get the #COM error seen in the attached images. Anything you you guys can think of would be greatly appreciated.

Thank you

I don't use this driver but looking at it it hasn't got an address in the IO device field, how does it know where the device is ?

Also you have the device memory field set to TRUE, this won't talk to anything ?
 

Similar Topics

Hi, I'm a first time poster. I need to establish a connection between an FX5U PLC to a Citect PC. I will be using a MODBUS TCP - MODBUS SERIAL...
Replies
8
Views
3,988
Hi guys, I have a client with a siemens S7200 PLC (1215C CPU),which has an on board ethernet port (marked "profinet" on the PLC) and I need to...
Replies
1
Views
1,537
Hi, Is there an easy way to zero all the data from a device when the comms fail? We pull data from some BACNet devices into the Redlion and then...
Replies
4
Views
3,078
has anyone found a successful citect native driver to establish successful comms with a ABB AC500 PLC for modbus on etherne
Replies
0
Views
1,448
need some fast help with getting comms to my I/O device Citect Compact Logix 1769-l33ER. i have another compact logix device that has been...
Replies
22
Views
6,775
Back
Top Bottom