Citect Comms to Compact Logix - Help !
Yes you are correct. many many thanks Andrew.
i am in middle of commissioning and the OEM has requested trends. i now have a variable successfully displaying so should be good now. i bow to your experience shame you are in sydney as i could use your services. your help has been extremely appreciated and much faster than schneider support which i do not have.
thanks again.
No problems, glad we got to the bottom of it.
If you ever do any ABCLX work in the future I recommend reading through the ABCLX help file (located in the Citect installation bin folder- ABCLX.chm)
And also enable logging and look at those log files, they do tell you alot.
will do as you suggest. i reckon the driver was root cause issue yesterday.
i changed the comms to backup server today in desperation and then made the typo doing that.
I know what its like mate, sometimes we make silly mistakes when commissioning and under a bit of presure.
Hope the rest of it goes well.
Thanks Again Andrew, set up multiple tag, alarms, graphics & trends & backup server I/O devices this morning with no further issues.
Much appreciated.
Hi, I'm a first time poster. I need to establish a connection between an FX5U PLC to a Citect PC. I will be using a MODBUS TCP - MODBUS SERIAL...
3,982
Hello All, I am running Citect SCADA 2018 R2 and trying to connect to a AB ControlLogix L81E. I have configured the board, port and IO device...
1,915
Hi guys, I have a client with a siemens S7200 PLC (1215C CPU),which has an on board ethernet port (marked "profinet" on the PLC) and I need to...
1,534
Hi, Is there an easy way to zero all the data from a device when the comms fail? We pull data from some BACNet devices into the Redlion and then...
3,069
has anyone found a successful citect native driver to establish successful comms with a ABB AC500 PLC for modbus on etherne
1,445