My current project is using a Modicon Quantum to control the belts and various processes in a coal proccessing plant. Relatively standard stuff. I am using RSView as the HMI for the operator and to process some data for a daily report, again fairly standard. My problem comes when I try to set the PLCs clock time from within RSView. The system tags will transmit to the PLC, but the clock value will not change. Do I need to use SBIT to set one (or more) of the clock register's bits before it will allow a write, and if so, which one?
Yes, there are bits that need to be set, in order to start/set the clock.
The first 4x clock register is the control register. The bits are:
1 - clock values are being set
2 - clock values are being read
3 - all clock values have been set
4 - error
To set the clock the bit pattern should be: 10000000000000000
To use the clock the bit pattern should be: 01100000000000000
(this looks weird but Modicon counts bits 1-16 left to right)
Thanks, Jim.
Actually I discovered this last night during a trip to the project site. I had found the information on the bits in the Block Library Users Guide, but it realy told me nothing but the respective bits basic function, as you show above. A little trial and error showed me the bit patterns I needed to achieve, from there it was all downhill to setting the logic to accomplish it.
I was online a SLC5/04 yesterday and one thing I did was go to processor properties and set the date and time to get the PLC clock current. It...
724
Hello PLCS.Net! I am trying to add a bunch of PLCs to the Logix5000 Clock update tool. It has an import feature which can import LST files...
1,001
What are the differences between AB "Clock Update Tool" Vs "Clock Sync Service"? Clock Update Tool seem to allow manual syncs along with scheduled...
1,203
Hi everyone :) We've got a ControlLogix5573 PLC that has it's time updated every day to an incorrect time. We've searched through PCs that we...
6,218
Hey guys, Quick question about the Clock Update Tool; I've got it set up on my runtime server to sync once a day with my local PLCs, and that's...
3,050