CLX tags over CNet
pcgray468
Oct 2008
Billings, MT
Hello again. I have asked a similar question before, but I may (and probably still) have worded it incorrectly. But....
I have worked with SLC and PLC5 that communicated to RSView on DH+, but I currently need to setup a CLX L61 v.16 for status and alarm annunciation of High Voltage breakers. This processor will be in slot (0) of a 10 slot chassis with a 1756-CN2 (node 10) and five (5) 1756-IH16I modules. Node 1 on the CNet is an operator's workstation running a HMI (I can only assume RSView).
I may be making this harder than it is, but do I need any MSG instructions to send the required tag values across the CNet. I have read about Produced/Consumed Tags, but I was wondering if I could just reference the tags (Base or alias) directly from the HMI. In SLC and PLC5 I could directly reference tags, but is this possible with the combination of CLX and CNET?
Thanks for any help.
I thought I was making this harder than it was. Thanks alot. I have already created alias tags for all the points I need, but I guess I really did not have to do this.
Thanks again
You're welcome. Your HMI can read either the base or alias tags. Setting up the communications in RSView32 is a little different (needs an OPC Node), but beyond that, there isn't really any difference.
OG
Hi, we have a Wonderware InTouch (v9.5) application that reads data from several older Compact/ControlLogix PLCs (v.15 firmware) using DASABCIP...
4,789
I have a UDT with 166 Members,part of which has the 40P module definition. As part of the upgrade from a PowerFlex 40P to a PowerFlex 525, this...
2,378
Just sharing an experience with a weird one that had 3 EE's scratching our heads for a bit... A PLC5 program was converted to CLX, version 20 in...
11,212
Traditionally I create buffer routines to read all inputs into a new tag, and conversely, the output buffers to the actual output tags. However I...
2,593
In a certain part of this program, we are looping through instances of a control module. The data is stored in a UDT array of 7 elements...
2,810