I'm struggling with intermittent comm loss on two ABB ACS800 Drives, it definitely seems to be affecting one drive more than the other but still both.
RSNetworx for ControlNet is not providing much help.
I've wrote automatic reset logic for the drives to help mitigate the issue.
It seems to happen sporadically every couple of months and the best information I've gotten from the manuals is to power down the drive to reinitialize the the module.
Once we have some sheduled downtime I plan on checking the connections and verifying the end of line resistor.
I would appreciate any help or comments.
The connections and verifying the end of line resistor is a good idea. Also ensure that the communication line is away from any high voltage lines.
You could also try to slow the communication baud rate down. Sometimes this will help with some noise or distance problems.
Regards,
Good Morning , I just recently did a project with several PowerFlex 525 drives. I just recently started getting a F 73 Fault ( EN Net Loss...
24
24,474
Easy, basic question... this is my first time linking 3 ABB vfds to an Allen-Bradley PLC using ethernet IP, and the odva Drive assemblies 123 and...
2,495
Hello, How can I go about setting up a fault bit if I lose comms to an AENTR module? I have several 1734 AENTR modules on my network. Some...
3,423
Processor is a L32E For some reason, I thought that there was a tag member that would give a status on Ethernet communications for a powerflex...
25
15,705
Quick question guys, I have a powerlfex 40 drive that intermittenly show an F081 fault...it clears and runs but comes up every once in while. This...
2,804