Comms fail action (M340 <-> STB NIP2212)
iJAF
Sep 2010
PT
Hi !
Hi have a M340 connected to several NIP2212 STBs !
If i disconnect the network cable from any STB, they enter in fail mode and make the predefined action (outputs to 1 or 0) immediately !!!
My question:
is there any way to delay 10 seconds the outputs from entering in fail mode ?! i.e. they only make the predefined action if the cable is disconnected more than 10 secs !
Thanks in advance !!
On the webpage for the NIP2212, select
Configuration -> Master Controller -> Holdup time
I didn't try it, but I expect this to delay fallback action.
Thank you !!! it worked :)
i was only checking in advantys and not in web configuration pages !!!