I know this issue has been raised before, but it wasn't really answered in the last thread http://www.plctalk.net/qanda/showthread.php?t=8940
I'm trying to get an upload from a SLC 5/05 connected to a GE Fanuc Quickpanel HMI. I've had to remove the RS232 connection to the HMI to get the upload. I connected to the PLC and tried to Auto-Configure the driver (serial driver) and am getting the message:
"unable to verify settings due to packet timeout! Check all cables and configuration and try again"
The auto-configure is getting as far as the parity check and then I get the message. The RS232 light on the controller is flashing when the PC is connected, but steady green when the HMI is connected.
I've tried using two different laptops and two comms cables. There is an ethernet port but I can't modify the IP address settings on the laptops to communicate this way.
Anybody recognise this message? What should I do?
Pablo2000
Your Quickpanel could be using DH485 protocol on the SLC-5/05 serial port, in which case you'd have to configure the "1747-PIC/AIC+" driver in RSLinx instead of the "RS232 DF1 Devices" driver.
Unfortunately, that "1747-PIC/AIC+" driver can be tricky (there are dozens of threads explaining it, mostly to people who can't spell COM1.) If you know how to do this, and you have a built-in RS232 port, you might spend a little time trying.
I'd recommend pursuing an Ethernet connection, even if it means getting your boss to let you use your tools.
I have an existing installation of panelview Plus 600 connected to SLC5/03 that has been working for the past couple of years. Recently the...
4,010
Hi All, I'm having difficulty establishing communication between a panelview plus compact 1000 and an SLC 5/05(processor 1747-L552). I can...
3,744
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
73
Hello everyone! I have a control logix plc that is set up to communicate with 6 1794-asb flex i/o racks. Everything has worked good over...
516
I have an AB 1769 L18ER which is connected to our plant network via NAT device RAM 6021. About a week ago, its connection to our Ignition...
371