Communicatin of WAGO with Automation Direct HMI

Siby

Member
Join Date
Jul 2006
Location
Dubai
Posts
27
Hi is there any special modbuus block in wago RTUs for establishing communication with Automation Direct HMI on modbus RTU.
Any guidlines will be appreciated.

Regards
 
You'll have to consult your WAGO manual for that info, they should provide a Register to Modbus Address Map for you to use. Then you'll need to create tags in the HMI using those addresses. Should be a simple operation, if you provided your actual part numbers than you might receive more help.
 
750-841
Controller
750-650Modbus RS232 module


The above are part numbers however im still struggling to find a solution

Regards
 
Siby,

First let me say that I know nothing about the wago controller.

But I do know if you are using serial comms, the HMI needs to be the master and the contoller needs to be the slave.

If you already know this, please disregard this post.
 

Similar Topics

Hi I am twido PLC TWDLCAA24DRF and HMI HMIS5T . Confugured HMI as master and twido as slave on modbus RTU. Parity none,stop bit1,data bit 8...
Replies
0
Views
1,304
Hi, can a have help? I vill reading special data from VEGAPULS to STEP 7 via HART analog modul. Read standards data via universal command is OK...
Replies
5
Views
3,378
i am currently working with the B & R plc with module name(CP360) of intel processor. and i want to establish the ethernet connetion between...
Replies
1
Views
4,567
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
94
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
130
Back
Top Bottom